Posted by Yvesabout 1 year ago
Over-Drilling of Holes (Embedment Depth)

-As per design, the required embedment depth is 200 mm. However, due to over-drilling, the hole ended up with a depth of 300 mm (an extra 100 mm).

Question:
-Can the extra 100 mm be filled with RE 500 V3, allowed to cure, and then proceed with installing the anchor at the correct 200 mm embedment depth?
-In this case, the bottom 100 mm epoxy would serve as a substitute for concrete. Is this acceptable?
-Kindly provide a technical reference supporting this approach, if available.

Over-Drilling,Holes,(Embedment,Depth)

1 Reply
Posted by Carlo Marte Redosendoabout 1 year ago

Hi Yves thank you for the question.

Yes it is possible to fill the hole with RE500v3 up to the desired depth as long as the concrete has a lower compressive strength compared to RE500v3 which has a compressive strength of 82.7Mpa. Make sure that the RE500v3 mortar will be fully cured before injecting again the new mortar. See attached screenshot for the compressive strength of the RE500v3.